Oil boiler is leaking water intermittently.

Discussion in 'The DIY Room' started by Warner, Mar 7, 2020.

  1. brenndatomu

    brenndatomu

    Joined:
    May 29, 2015
    Messages:
    20,560
    Likes Received:
    128,121
    Location:
    NE Ohio
    That is a little high if the boiler is cold...fine if it's hot. I usually set cold pressure to more like 12-15 PSI.
     
    TurboDiesel and Horkn like this.
  2. Horkn

    Horkn

    Joined:
    Dec 17, 2014
    Messages:
    27,049
    Likes Received:
    150,973
    Location:
    SE Wisconsin
    True, when I was saying 20 psi is fine, I meant when running and to to Temp. If that's the cold psi, that could be the issue.
     
  3. billb3

    billb3

    Joined:
    Oct 7, 2013
    Messages:
    9,820
    Likes Received:
    50,421
    Location:
    SE Mass
    When the system is hot the expansion tank should be hot except for where the bladder is. It should be half water, half bladder. Warm water, cool bladder.
    The bladder pressure should stay at about 12-15 psi if you relief the water pressure. If it goes to nothing the bladder is shot.
    If the pressure relief was blowing off because the pressure was high it was doing its job. Is the pressure regulator adjustable ? They do go bad.
    It might be more common for screens in them to block and pressure go low, but they can leak at a seal and go high as well. Or just jam.
     
    Last edited: Mar 8, 2020
    brenndatomu likes this.
  4. Warner

    Warner

    Joined:
    Jun 19, 2017
    Messages:
    6,557
    Likes Received:
    41,505
    Location:
    New Hampshire
    The boiler was hot when I checked the gauge. I am suspecting the bladder went that would explain “tire going flat” noise the wife herd. I would expect water to come out when I checked the pressure tho? I’ll get my temp gun out and check the tank today.

    The relief valve that is spewing water out intermittently was replaced yesterday.
     
  5. Warner

    Warner

    Joined:
    Jun 19, 2017
    Messages:
    6,557
    Likes Received:
    41,505
    Location:
    New Hampshire
    One thing that i have noticed is we haven’t been hearing the pipes banging(water hammer) when the washing machine is running like we did before the noise/leak incident.
     
    brenndatomu and TurboDiesel like this.
  6. Mitch Newton

    Mitch Newton

    Joined:
    Oct 4, 2013
    Messages:
    905
    Likes Received:
    3,362
    Location:
    Beavercreek, Ohio
    Interesting that you say "Pipes Banging". We had the same leak on the pressure relief value. The tech replaced the water tank. The value still leaked. Then he finally replaced the value and cured the leak. However, we still had severe pipe banging. We noticed that water was not circulating in the radiators. They weren't getting hot. We replaced the pump and all is fine now.
     
    brenndatomu and stuckinthemuck like this.
  7. TurboDiesel

    TurboDiesel

    Joined:
    Nov 22, 2013
    Messages:
    16,054
    Likes Received:
    95,675
    Location:
    Hollidaysburg Pa
    The washer and the boiler aren't connected in any way, don't know why there'd be any change...
     
    Last edited: Mar 8, 2020
    brenndatomu likes this.
  8. Warner

    Warner

    Joined:
    Jun 19, 2017
    Messages:
    6,557
    Likes Received:
    41,505
    Location:
    New Hampshire
    The hot water for the washing machine comes from the boiler? Forgive me I know little about this stuff.
     
    brenndatomu and TurboDiesel like this.
  9. TurboDiesel

    TurboDiesel

    Joined:
    Nov 22, 2013
    Messages:
    16,054
    Likes Received:
    95,675
    Location:
    Hollidaysburg Pa
    Yes your domestic hot water comes from your boiler.
    I would guess the pipes rattle because the washer has a solenoid valve that slams shut when full. Or a couple times during the cycle
     
    brenndatomu likes this.
  10. TurboDiesel

    TurboDiesel

    Joined:
    Nov 22, 2013
    Messages:
    16,054
    Likes Received:
    95,675
    Location:
    Hollidaysburg Pa
    Pipes usually rattle because they're not fastened properly. Ie; not enough pipe hangers
     
    stuckinthemuck and brenndatomu like this.
  11. Warner

    Warner

    Joined:
    Jun 19, 2017
    Messages:
    6,557
    Likes Received:
    41,505
    Location:
    New Hampshire
    I just mentioned it thinking it may be related. It could be we are hearing it less because the ground is thawing. The noises around the house seem to change with the season.
     
  12. Warner

    Warner

    Joined:
    Jun 19, 2017
    Messages:
    6,557
    Likes Received:
    41,505
    Location:
    New Hampshire
    Green valve was replaced yesterday
     
    stuckinthemuck and brenndatomu like this.
  13. Warner

    Warner

    Joined:
    Jun 19, 2017
    Messages:
    6,557
    Likes Received:
    41,505
    Location:
    New Hampshire
    My ir temp gun is at work with the rest of my tools! Grrr...
    The tank feels to be the same temp top to bottom(cool). And tapping on it it sounds empty top to bottom.
     
    stuckinthemuck and TurboDiesel like this.
  14. brenndatomu

    brenndatomu

    Joined:
    May 29, 2015
    Messages:
    20,560
    Likes Received:
    128,121
    Location:
    NE Ohio
    Not unless the bladder has a catastrophic failure...which they usually just leak enough to "let the air out" and not so much "fill with water" on the air side...there may be some in there, but not full enough to leak out when you check the pressure. Some systems use an expansion tank that doesn't even have bladder in it...just an air pocket in the top of the tank...have one at work like that. I checked with the OEM to see if they recommend a "new style" bladder tank, they said nope, we still use the same one you have.
    I assume the relief valve is rated at 30 PSI?
    Do you mess with the relief valve much? Its kind of a catch 22 situation with those...you need to operate it manually once in a while to make sure it is free and can do its job if needed, but any time the valve is lifted off its seat there is the risk of a piece of dirt/contamination getting in there causing a leak, (slow drip like you had there) and I have rarely had any luck getting one to seal again once they have started leaking.
     
  15. don2222

    don2222

    Joined:
    Nov 10, 2013
    Messages:
    3,263
    Likes Received:
    4,422
    Location:
    Salem NH
    You can get a cold water pressure tank. We have one.
    $27 bucks @ Home Depot 40 PSI works up to 150 PSI - See pics below
    Eastman 2 Gal. Thermal Expansion Tank-60022 - The Home Depot
     

    Attached Files:

    stuckinthemuck and brenndatomu like this.
  16. Warner

    Warner

    Joined:
    Jun 19, 2017
    Messages:
    6,557
    Likes Received:
    41,505
    Location:
    New Hampshire
    I have never touched the valve in the 5 years we have lived here dad said he never did anything with it either. 8772C898-3D28-42D6-92ED-CF37C27CA026.jpeg Here is the best pic I could get of the valve. There was no water on the floor this morning....
     
    brenndatomu and TurboDiesel like this.
  17. Warner

    Warner

    Joined:
    Jun 19, 2017
    Messages:
    6,557
    Likes Received:
    41,505
    Location:
    New Hampshire
    08E6B179-A1DF-4723-A35B-80856639C91B.jpeg Inside the old valve
     
    brenndatomu and TurboDiesel like this.
  18. TurboDiesel

    TurboDiesel

    Joined:
    Nov 22, 2013
    Messages:
    16,054
    Likes Received:
    95,675
    Location:
    Hollidaysburg Pa
    I never touch the relief valve on a water heater because of that. Not even when new
     
    Mitch Newton and brenndatomu like this.
  19. brenndatomu

    brenndatomu

    Joined:
    May 29, 2015
    Messages:
    20,560
    Likes Received:
    128,121
    Location:
    NE Ohio
    Yup, I'm with ya there...but we have to get annual state boiler inspection on the big one at work (digester heater) and the inspector always checks/lifts the relief valve! :eek: :picard: (I think he owns stock in a relief valve company! :rofl: :lol:)
     
    TurboDiesel likes this.
  20. brenndatomu

    brenndatomu

    Joined:
    May 29, 2015
    Messages:
    20,560
    Likes Received:
    128,121
    Location:
    NE Ohio
    Hmm...I'm surprised that has a 150 PSI valve in it...is that common on residential boilers? With one rated that high then the old one was certainly bad...I thought maybe you were just "dancing the dance" between cold/hot system pressures and had a 30 PSI relief valve...I've only ever messed with commercial systems so residential might have different rules to play by...