Generator Transfer Panel

Discussion in 'Everything Else (off topic)' started by thewoodlands, Apr 21, 2015.

  1. thewoodlands

    thewoodlands

    Joined:
    Oct 3, 2013
    Messages:
    15,040
    Likes Received:
    62,334
    How can you tell if an existing Generator Transfer Panel can handle a higher watt generator?

    Inside the Generator Transfer Panel it says 35A ..... 120 ..... 18A .... 240 .... 30A Max.

    We have a 4200 watt portable generator but we're thinking about getting a 8000 running - 10,000 start .... watt generator.

    We do want to put more on the panel so we might need a bigger one.
     
    wildwest and My IS heats my home like this.
  2. Stinny

    Stinny

    Joined:
    Oct 29, 2013
    Messages:
    14,138
    Likes Received:
    60,664
    Location:
    western Maine
    A 10,000 watt gen is a little under 50 amps @ 240 volts, 100 amps @ 120 volts. You'll need a 50 amp / 240 volt transfer panel rating.
     
    Last edited: Apr 21, 2015
  3. KaptJaq

    KaptJaq

    Joined:
    Oct 11, 2013
    Messages:
    721
    Likes Received:
    3,567
    Location:
    Long Island, NY
    When you are on the generator how much do you plan on using? We have a 6,500/8,000 watt generator and, with the whole house running, it rarely runs hard. We probably stay under 3,000 watts.

    The box you have now is properly rated for the 4,000 watt generator. Anything larger will pop the generator breaker in the transfer box if you push it.

    KaptJaq
     
  4. thewoodlands

    thewoodlands

    Joined:
    Oct 3, 2013
    Messages:
    15,040
    Likes Received:
    62,334
    Thanks for the replies, we'll be getting an estimate for a new one.
     
    eatonpcat and Stinny like this.
  5. Gary_602z

    Gary_602z

    Joined:
    Oct 4, 2013
    Messages:
    2,464
    Likes Received:
    12,340
    Location:
    Lake Odessa, Michigan
    Are you going with a standby unit? I had to put one in at work. I should have done it years ago, my hair wouldn't be as gray as it is now!

    Gary
     
    eatonpcat and papadave like this.
  6. thewoodlands

    thewoodlands

    Joined:
    Oct 3, 2013
    Messages:
    15,040
    Likes Received:
    62,334
    A portable generator.
     
    papadave likes this.
  7. My IS heats my home

    My IS heats my home

    Joined:
    Dec 1, 2013
    Messages:
    7,394
    Likes Received:
    17,655
    Location:
    Albany, NH
    While you guys are talking genny's, is natural gas quiter than gas or diesel?
     
  8. Gary_602z

    Gary_602z

    Joined:
    Oct 4, 2013
    Messages:
    2,464
    Likes Received:
    12,340
    Location:
    Lake Odessa, Michigan
    Our 20kw Kohler standby on propane is a lot quieter then a 6500 gas portable that we have. That said some of the Hondas are quiet and I borrowed a 5000 watt portable from one of by drivers that was fairly quiet.

    Gary
     
    My IS heats my home and Stinny like this.
  9. basod

    basod

    Joined:
    Nov 4, 2013
    Messages:
    5,048
    Likes Received:
    20,841
    Location:
    Mount Cheaha AL
    If you're putting in a portable "not on demand start system"
    the generator @10kW max - is an advertising gimmick, 8kW will max it out - basically what the motor could tolerate for normal fuel consumption rates, or generator winding insulation

    The switching disconnect isn't really the main concern in swapping this over - its the feeder cable from the sub panel to the disconnect, probably 10ga rated for 30amps in it's current configuration
    The feeder cable will need to be upsized in addition to the switch(is has an interrupting rating and internal conductors are probably capable of carrying the current)
     
  10. MasterMech

    MasterMech The Mechanical Moderator

    Joined:
    Oct 2, 2013
    Messages:
    9,648
    Likes Received:
    26,040
    Location:
    Greenville County SC
    Check the output options of the genny. An 8k/10k may not have a 50A output. In which case a 30A setup should be fine.
     
    Last edited: Apr 25, 2015
    wildwest and thewoodlands like this.
  11. thewoodlands

    thewoodlands

    Joined:
    Oct 3, 2013
    Messages:
    15,040
    Likes Received:
    62,334
    They came up to give us a estimate, about all we need is a new transfer panel if that along with a new whip.

    They still haven't emailed us the estimate but we're hoping to get that this week.
     
    wildwest, MasterMech and Stinny like this.
  12. rottiman

    rottiman

    Joined:
    Oct 4, 2013
    Messages:
    14,437
    Likes Received:
    95,936
    Location:
    XXXXXXXXXXX
    I have a 5000 Honda running on propane. Same noise level but runs a whole lot smoother on propane.
     
    wildwest and thewoodlands like this.
  13. thewoodlands

    thewoodlands

    Joined:
    Oct 3, 2013
    Messages:
    15,040
    Likes Received:
    62,334
    The contractor called this morning when I was in the woods with the price, we thought the price was good so we'll go with it.

    He'll be putting in an outlet in the floor for my wife and we'll have a new (bigger) Transfer Panel for the generator.

    Hopefully we can get this done before our storm season (high winds) begins which is usually by the end of May thru August.

    From my talks with the electrician, he thinks we can have power to everything and then we'll control what we want on or off.

    Our old generator is from 1998, bought before the ice storm hit. It has been a good little generator so we'll keep it for a back up.
     
    papadave and wildwest like this.
  14. thewoodlands

    thewoodlands

    Joined:
    Oct 3, 2013
    Messages:
    15,040
    Likes Received:
    62,334
    The contractor just called back, he's ordering everything he needs Monday. The power company will have to shut off the power when he's ready so we'll see how long that will take.
     
    Stinny and papadave like this.
  15. thewoodlands

    thewoodlands

    Joined:
    Oct 3, 2013
    Messages:
    15,040
    Likes Received:
    62,334
    The contractor called me again, everything is in for the transfer panel but we're waiting on a floor outlet to come in which should be Wednesday or Thursday.

    Our storm season (high winds) is getting closer so it will be nice to get the new transfer panel in.
     
    papadave and Stinny like this.
  16. thewoodlands

    thewoodlands

    Joined:
    Oct 3, 2013
    Messages:
    15,040
    Likes Received:
    62,334
    We just received a call from our contractor, June 1st is the date he'll do everything.
     
    papadave and Stinny like this.
  17. papadave

    papadave

    Joined:
    Oct 3, 2013
    Messages:
    18,181
    Likes Received:
    82,470
    Location:
    Right where I want to be.
    That's great zap.
    How long did he say it'll take?
     
    Stinny likes this.
  18. thewoodlands

    thewoodlands

    Joined:
    Oct 3, 2013
    Messages:
    15,040
    Likes Received:
    62,334
    He seems to think just the one day. The power company said they would be here to shut the power off at 8:30 a.m.
     
    papadave likes this.
  19. thewoodlands

    thewoodlands

    Joined:
    Oct 3, 2013
    Messages:
    15,040
    Likes Received:
    62,334
    The job got done today, power for the whole house when we lose it.

    We will have to watch what we are running if we want to use the hot water heater.
     
  20. papadave

    papadave

    Joined:
    Oct 3, 2013
    Messages:
    18,181
    Likes Received:
    82,470
    Location:
    Right where I want to be.
    Wow, someone who followed through on doing what he said he'd do and when.
    Gotta' be a nice feeling getting that done zap. Very cool.
     
    thewoodlands and Stinny like this.