Enviro convection blower noise

Discussion in 'Pellet Stoves, Pellet Fireplaces, Pellet Furnaces' started by Laborer22, Jan 30, 2016.

  1. Laborer22

    Laborer22

    Joined:
    Oct 14, 2015
    Messages:
    4
    Likes Received:
    11
    Location:
    Revere,ma
    Hi everyone.I replaced my convection blower 2 weeks ago on my Vistaflame VF100.Purchased it through my dealer and I installed it without any issues.My problem is it's very loud at it's lowest speed.I plugged it in to my variac transformer,and it rattled until I got it to about 70 volts.after that it's quiet. The noise is in the motor itself,not the squirrel cage.Is this what I am to expect,or am I missing something? Everything is tight in the stove. I've been playing phone tag with the dealer so I haven't had a chance to speak to him. Thanks in advance for taking the time to help me.
     
    ivanhoe and wildwest like this.
  2. slvrblkk

    slvrblkk

    Joined:
    Oct 6, 2013
    Messages:
    6,647
    Likes Received:
    29,535
    Location:
    Northampton, PA
    Not sure if this helps you out or not but I have a Fasco A120 convection fan that replaced the original fan that started having a slight bearing noise. The damm Fasco has a weird harmonic noise coming out of the motor on low only. So I order a Rotom and that one if super quiet so I'm not sure what is up with the Fasco.
     
  3. Laborer22

    Laborer22

    Joined:
    Oct 14, 2015
    Messages:
    4
    Likes Received:
    11
    Location:
    Revere,ma
    Thanks for the quick reply.Harmonic is exactly the noise I have.I may order another brand also because the noise is annoying.Thanks for the help.
     
  4. subsailor

    subsailor

    Joined:
    Oct 17, 2013
    Messages:
    3,693
    Likes Received:
    14,973
    Location:
    Winthrop, Maine
    I have the same problem with my distribution blower. I replaced the original with the same Dayton blower. It's quiet on low and max but has a loud, annoying, harmonic whine in between. Annoying enough where I'll probably replace it again next year.
     
  5. imacman

    imacman

    Joined:
    Oct 23, 2013
    Messages:
    6,633
    Likes Received:
    27,528
    Location:
    Denver, NC
    Welcome to the forum Laborer :handshake:
     
  6. Laborer22

    Laborer22

    Joined:
    Oct 14, 2015
    Messages:
    4
    Likes Received:
    11
    Location:
    Revere,ma
    Thank you Imacman.It's a pleasure to be here.
     
    ivanhoe, slvrblkk and imacman like this.
  7. eatonpcat

    eatonpcat

    Joined:
    Oct 5, 2013
    Messages:
    10,283
    Likes Received:
    58,507
    Location:
    Eaton Township, OH
    X2
     
    ivanhoe and Laborer22 like this.
  8. Snowy Rivers

    Snowy Rivers

    Joined:
    Nov 15, 2015
    Messages:
    2,849
    Likes Received:
    12,491
    Location:
    Newberg, Oregon
    Dirty voltage

    As mentioned, it is a harmonic that is caused by the voltage cycles not being perfect.

    Many of the triacs used in these stoves are trash and do not put out a good clean wave form.

    If the wave is not exactly the same above and below the line (Scope pattern) the motor will make WA WA WA WA WA NOISES

    It is not the motor, it is the triac (Speed control)

    Best advice is to find a happy spot and leave it there.
     
    ivanhoe, Laborer22 and imacman like this.
  9. Laborer22

    Laborer22

    Joined:
    Oct 14, 2015
    Messages:
    4
    Likes Received:
    11
    Location:
    Revere,ma
    Hi Snowy. Thanks for the reply. I hooked the motor up to it's own independent power source through a variac autotransformer. still get the same hum until it gets about 70 volts, then it quiets down somewhat when I increase the voltage .also I never had this issue with the motor I replaced. as far as finding a sweet spot,I don't have that luxury. My convection blower changes speeds when I change the heat level .I can't control it independently. I spoke with the dealer this morning. Still waiting for a call back.
     
    ivanhoe and imacman like this.
  10. Snowy Rivers

    Snowy Rivers

    Joined:
    Nov 15, 2015
    Messages:
    2,849
    Likes Received:
    12,491
    Location:
    Newberg, Oregon
    Hmmmmm

    Ok
    Swap the motor out for an open frame style.

    These tend to be a lot quieter.

    The issue is the control board and the speed control that's built in is sending out dirty current.

    There is the choice of tapping into mainline voltage and using a stand alone speed controller to tun the fan.

    Easy fix if you want to do that.

    70 volts on these motors is about the low limit to keep them rolling along properly.

    My new controller has a resistor across the terminals to stop the fan from going below 75 volts

    Good luck
     
    ivanhoe and imacman like this.
  11. slvrblkk

    slvrblkk

    Joined:
    Oct 6, 2013
    Messages:
    6,647
    Likes Received:
    29,535
    Location:
    Northampton, PA
    My original convection blower was quiet through all speeds, the only thing was the one bearing was getting noisy. I replaced that with a Fasco A120 (original was a Jakel). The Fasco has a steady harmonic on low only, other speeds were fine. I ordered a Rotom replacement and this one is completely quiet on all speeds like the original so who the heck knows.
     
    ivanhoe and imacman like this.
  12. Snowy Rivers

    Snowy Rivers

    Joined:
    Nov 15, 2015
    Messages:
    2,849
    Likes Received:
    12,491
    Location:
    Newberg, Oregon
    Every so often you will see a motor that's noisy and no manner of fooling withe it will make it Quiet.

    The open frame motors with the heavy magnet bars are far better motors and less likely to wa wa wa wa.
     
    ivanhoe, imacman and slvrblkk like this.
  13. Snowy Rivers

    Snowy Rivers

    Joined:
    Nov 15, 2015
    Messages:
    2,849
    Likes Received:
    12,491
    Location:
    Newberg, Oregon
    The practice the manufs have started of controlling the fan speeds with the feed rates is another CYA tactic.

    So many people will not bump the room air fan up where it should be when they are stoking the thing hard and then overheat the beast.

    Our Big Whit has had a pretty much full speed fan since we got it and I really like the speed.

    Going to engineer the new control to get the thing right in that sweet spot.

    It's not ungawdly loud, but puts out a good volume of air.

    The harmonic sounds though can drive ya nuts.

    We get times when the line voltage will be a tad higher or lower coming into the house and when this happens the old Whit really sings.

    Then it stops and is quiet again ?????

    A fresh room air fan is likely in the offing me thinks
     
    ivanhoe, imacman and slvrblkk like this.