    Quick overview.... Long ranch, large open concept living room, dining room, & kitchen. Tstat in the living room. Past the living room, long hallway, 2nd bedroom, washer/dryer closet, the oil blower system, bathroom, then master bedroom at the end. Living room temps after running the woodstove overnight 64. Far bathroom and master bedroom, 58. Too much hustle and bustle in the a.m. to have heat from the woodstove make its way back to the colder part of the house, fans work, but take awhile.

    My question is, how can I run a sencond thermostat in the rear of the house? My thinking is, to splice off of the wires going to the tstat in the living room and adding them to the second tstat. Will this work?

    I understand that the heat would come into the already warm parts of the house, and I plan on shutting down a couple vents.

    Any advice appreciated!:)
     
    Stinny likes this.
  2. lukem

    lukem

    Joined:
    Oct 4, 2013
    Messages:
    11,817
    Likes Received:
    63,100
    Location:
    IN
  3. jetjr

    jetjr

    Joined:
    Feb 24, 2014
    Messages:
    3,233
    Likes Received:
    8,953
    Location:
    Pa/Md line
    Curious on this one too. Would a small electric heater just to heat the bedroom and bathroom work better for you?
     
    Chvymn99, Stinny and Well Seasoned like this.
  4. Stinny

    Stinny

    Joined:
    Oct 29, 2013
    Messages:
    14,113
    Likes Received:
    60,513
    Location:
    western Maine
    All the old style mercury therms did was act like a simple switch on and off. I assume the newer ones do too, but maybe not. If they do then yes, you can parallel wire in a second therm and put it in a different area. Then, the therm that is set the highest will fire the furnace.
     
    Well Seasoned likes this.
  5. Stinny

    Stinny

    Joined:
    Oct 29, 2013
    Messages:
    14,113
    Likes Received:
    60,513
    Location:
    western Maine
    I was thinking that too. Those quartz units work well and aren't hot to the touch... so child safe.
     
    jetjr and Well Seasoned like this.
  6. Well Seasoned

    Well Seasoned Administrator

    Joined:
    Oct 3, 2013
    Messages:
    18,038
    Likes Received:
    83,785
    Location:
    N.H. WMNF
    It would, but the dogs stay in the hall during the day and dont like messing with space heaters.
     
    jetjr and Stinny like this.
  7. Jack Straw

    Jack Straw

    Joined:
    Oct 3, 2013
    Messages:
    8,396
    Likes Received:
    52,391
    Location:
    30 miles west of Albany Ny
    It sounds like the new t stat is closer to the oil blower than the old t-stat, why not just run the new t-stat to the blower?
     
    Well Seasoned likes this.
  8. Well Seasoned

    Well Seasoned Administrator

    Joined:
    Oct 3, 2013
    Messages:
    18,038
    Likes Received:
    83,785
    Location:
    N.H. WMNF
    That is an option, but i figure why not just add another??? The one tstat is between the living room and dining room so being open concept and better insulation in that area, tstat wont trip really ever. Id like to add a second one at the other end of the house that would be closer to the oil heater, yet 30+ft from the opposing tstat.
     
    Stinny likes this.
  9. Norky

    Norky

    Joined:
    Oct 20, 2013
    Messages:
    972
    Likes Received:
    3,083
    If you have a timer on your existing thermostat, you can set it to come on at the time when you need it and have it set at a higher temp than usual.
     
    Well Seasoned likes this.
  10. jetjr

    jetjr

    Joined:
    Feb 24, 2014
    Messages:
    3,233
    Likes Received:
    8,953
    Location:
    Pa/Md line
    Makes sense about the dogs. I was blinded by my house having thermostats in every room. Darn electric heat.
     
    Well Seasoned likes this.
  11. Norky

    Norky

    Joined:
    Oct 20, 2013
    Messages:
    972
    Likes Received:
    3,083
    You could put a second thermostat in and install an A/B switch to toggle between the two.
     
    Well Seasoned likes this.
  12. Well Seasoned

    Well Seasoned Administrator

    Joined:
    Oct 3, 2013
    Messages:
    18,038
    Likes Received:
    83,785
    Location:
    N.H. WMNF
    I can set it to kick on at specific times, but the problem still exists. The stove room stays warm enough that I would need to guess the temps to set it at. For example, the tstat currently shows 74 in the dining room and the back bedroom is a cool 58. (Im off today) but those temps are a bit chilly for the chihuahua. Then, once the stove would go cool, the oil would run nearly non stop during the colder months. Again, if I have a second tstat, im only heating the back area due to closing some vents out front, and the oil wouldnt be on as much.
     
    Stinny likes this.
  13. Well Seasoned

    Well Seasoned Administrator

    Joined:
    Oct 3, 2013
    Messages:
    18,038
    Likes Received:
    83,785
    Location:
    N.H. WMNF
    What is an a/b switch? Electrical is not my specialty......
     
  14. Norky

    Norky

    Joined:
    Oct 20, 2013
    Messages:
    972
    Likes Received:
    3,083
    It's a switch that allows you to choose separate devices in a circuit. I don't think you'd need to be an electrician to figure it out.
     
    Well Seasoned likes this.
  15. bocefus78

    bocefus78

    Joined:
    Oct 14, 2013
    Messages:
    3,694
    Likes Received:
    19,839
    Location:
    Indiana
    This exactly. You are going to need to turn the power off to the old one, for the new one to work. You cannot have 2 tstats on the same circuit in my limited HVAC knowledge.

    The switch is basically like a boat battery switch (best example I could think of. ) So you can switch from 1 battery or the other.
    The tstat is low voltage wiring. 4 wires if I remember correctly. You need to find the hot, and install a switch on that wire that will determine if the power goes to the old tstat, or the new one.
     
    Well Seasoned likes this.
  16. Well Seasoned

    Well Seasoned Administrator

    Joined:
    Oct 3, 2013
    Messages:
    18,038
    Likes Received:
    83,785
    Location:
    N.H. WMNF
    I cant? Even if I parrarelled the wire?
     
  17. bocefus78

    bocefus78

    Joined:
    Oct 14, 2013
    Messages:
    3,694
    Likes Received:
    19,839
    Location:
    Indiana
    Ok, I had to google search because I am considering this also. Looks like you CAN install 2 tstats in parallel, but only 1 will work at a time. Lets say tstat1 is set at 70. tstat 2 is set at 75. When running heat, its going to shut off at 70, not 75.

    you can do 1 of 3 things from my whopping 10 minutes of research.

    1. Zone system. Expensive. Must replace equipment. Not worth it IMO.
    2. Install 2nd tstat in new location and a toggle switch to determine which tstat is used at the current time.
    3. Install new tstat in old location, but get one that has another sensor and mount this in new location. These units then AVERAGE the temps between the 2, and control the furnace with the AVERAGE temps seen between the 2 sensors.
     
    Well Seasoned likes this.
  18. lukem

    lukem

    Joined:
    Oct 4, 2013
    Messages:
    11,817
    Likes Received:
    63,100
    Location:
    IN
    3 sounds cool. Remote sensor is really what he's after.
     
    Well Seasoned likes this.
  19. Well Seasoned

    Well Seasoned Administrator

    Joined:
    Oct 3, 2013
    Messages:
    18,038
    Likes Received:
    83,785
    Location:
    N.H. WMNF
    Thanks for your research........Option 3 does sound ideal, especially if the 1st t stat will shut things down anyway or prevent the second one from even kicking in. The overall best bet may be to just move the original tstat to where I want to mount the second one..........uggghhhh.:confused:
     
    Stinny likes this.
  20. Stinny

    Stinny

    Joined:
    Oct 29, 2013
    Messages:
    14,113
    Likes Received:
    60,513
    Location:
    western Maine
    If you had a buddy who could take 10 minutes to look at what you have, it sure would help. I have done what you proposed... using 2 thermostats, wired in parallel... but, it was with the older mercury 2 wire thermostats. When we wanted to control the heat in one spot, we'd just turn the other one down. No AB switch. The higher set thermostat controlled the furnace.
     
    Well Seasoned likes this.