Generator house hookup - Q for electricians
Discussion in 'The DIY Room' started by bushpilot, Oct 7, 2015.
  1. bushpilot
    bushpilot
    Eastern Washington
    My portable generator has a bonded neutral (to ground). I want to hook this unit up to the house, and have already installed an interlock to ensure there is no back feed. The neutral is not switched by the interlock, only the two hots; the neutral is hard wired.
    Because there is a connection to ground in the main panel, I understand it should be floating on the generator, to avoid them being tied together in two places. But when using the generator as a portable unit, they should be bonded. So I don't want to break the bond at the generator.
    My planned solution it to not connect the ground wire at the inlet receptacle (on the house), and only connect the two hots and the neutral to the house. This will eliminate any loops, without modifying the generator itself.
    What thickest ye?
    Greg
  2. Eric VW
    You sayin' I'm fat?:rofl: :lol:
    IDK about this neutral thing... I'll ask a fella here at work...
    raybonz and wildwest like this.
  3. bushpilot
    bushpilot
    Eastern Washington
    Stupid spell check ... thinkest is the word.
    Greg
  4. wildwest
    OR was he talking about your thick skull?
  5. wildwest
    Thymbolic made me chuckle too :thumbs:
  6. raybonz
    raybonz Moderator
    Carver, Mass.
    I connected both phases, neutral and ground from the service panel to the outlet that the generator plugs into.. This would ground the generator frame and protect you in the event the frame became live. What you don't want to do is run a separate ground but use the one from the service panel.. A live generator frame could be a deadly hazard..
    Reliance Controls 30 Amp 10 Circuit Manual Transfer Switch Kit-31410CRK - The Home Depot
    basod, Well Seasoned and wildwest like this.
  7. bushpilot
    bushpilot
    Eastern Washington
    Thank you. But I am not sure this is right - nor am I sure it is wrong. The problem I see with what I understand you did, is that the ground and neutral on the generator cord are now parallel circuits. So the "return" from the neutral of the house will go through both the ground wire and the neutral to the generator. This would increase the chance of shock, rather than decrease it, could cause havoc with GFCIs, etc.
    I think most people do it as you suggest, and it works fine.
    I am thinking the best plan is to do as I was thinking, but then physically ground the generator, separate from the house. But I am still listening, thanks for the input.
    Greg
  8. raybonz
    raybonz Moderator
    Carver, Mass.
    Sorry forgot to mention this.. Found online to save typing:
    "Most portable generators are bonded neutral. The reason being is the unit then is grounded to the frame so there is no shock hazard. Manufacturers know that most consumers use them as without grounding them properly due to their portability. They should be changed to floating neutral when you are installing to the transfer switch."
    Well Seasoned likes this.
  9. bushpilot
    bushpilot
    Eastern Washington
    THANK YOU!
    So, I am thinking that my idea of not carrying the ground through to the house panel accomplishes the same purpose, without generator modification?
    Greg
  10. raybonz
    raybonz Moderator
    Carver, Mass.
    You avoid the neutral problem but leave the generator ungrounded.. You could attach a ground wire from the generator to the ground rod your service uses or break the ground to neutral connection at the genny.. Whatever works for you..
    WeldrDave and bushpilot like this.
  11. basod
    basod
    Mount Cheaha AL
    Greg if you want to be able to keep portability of the generator and break the neutral-ground bond for house use look into a simple knife switch disconnect that could be worked into wiring of the generator.
    You could use a single pole of an HVAC service disconnect.
    bushpilot and WeldrDave like this.
  12. WeldrDave
    Greg, You can also "dead spike" a grounding bar in the ground or your houses grounding bar and run a heavy alligator clip/connection to it if you choose to the frame of the generator. But Ray has a good point, you can leave it ungrounded. I'm not an electrical engineer but I have shocked myself once or twice!:rofl: :lol:
    bushpilot, basod, raybonz and 2 others like this.
  13. raybonz
    raybonz Moderator
    Carver, Mass.
    IMG_0684.JPG OK so thanks bushpilot for reminding me to remove the ground to neutral jumper on my generator.. I am a licensed electrician so I know better than this! I simply forgot to remove the jumper.. It took all of 10 minutes and this jumper is located in the generator head which is removed by 2 small bolts then remove the white wire that goes to the ground screw and winding.. I verified before and after with my multimeter then hooked up the generator to the transfer outlet and checked voltages.. All looked fine (which it did before) and took a shower with the furnace for hot water and the well pump on to create load and all is well.. Attached pics to show this wire I removed.. Easy to put back if I ever wanted to run the generator without transfer switch..
    Ray
  14. basod
    basod
    Mount Cheaha AL
    After seeing Ray's pictures it'd be real easy to add an automotive toggle switch to the peckerhead of the generator, just use the same size wire to increase the length of the leads, couple spade and ring terms and you're in business.
    bushpilot, raybonz and wildwest like this.
  15. raybonz
    raybonz Moderator
    Carver, Mass.
    Did think about this but will probably always connect to the transfer outlet plus very easy to reinstall the jumper..
    basod, bushpilot and wildwest like this.
  16. basod
    basod
    Mount Cheaha AL
    easier to flip a switch than mess with tiny screws when the power goes out;)
    raybonz likes this.
  17. raybonz
    raybonz Moderator
    Carver, Mass.
    True but I only use the generator plugged into the transfer outlet ..
    basod likes this.