    Hello all , I have a Quadrafire CB 1200 with the standard thermostat should I upgrade ?
     
    Papelletman and DexterDay like this.
  2. DexterDay

    DexterDay Administrator

    Joined:
    Oct 2, 2013
    Messages:
    12,411
    Likes Received:
    31,636
    Location:
    Northeast Oh
    Yes. A Hunter stat or Lux 500 or 1500 will have a bigger swing setting. If the Quad starts back up with just a short shut down, the thermocouple will not drop below 500° and the stove will overfeed at start up and sound like a freight train and look like a nuclear bomb!

    The Lux can get as much a 4.5° swing or 2.25° on each side of the setting.

    So if it's set at 70° the stove will start up at 67.75° and shut down at 72.25°. This gives the Quad ample time to drop in internal temperature (thermocouple). Also, if the stove is set to a lower setting (Low or Med) the stove runs longer and gives the house a better "soak" of the heat. I actually ran my 1200 on Low almost 24/7 in the dead of the winter. Kept my 2,100 sq ft house a nice even temp and the stove didn't start and stop 20 times a day. On start up, the stove runs on High until the thermocouple meets the 500° temp then the stove reverts to the setting you have it at. So running on low saves fuel if the stove has to start several times in one hour.

    That is why a large swing helps if running a stat. Let the stove work. Then give it a good rest.
     
    gbreda, slvrblkk, will711 and 2 others like this.
  3. Papelletman

    Papelletman

    Joined:
    Sep 10, 2015
    Messages:
    71
    Likes Received:
    343
    Location:
    Plymouth Meeting Pa.
    X2

    I also have a CB1200 with a Lux 1500u Thermostat set at 2° swing
     
    don2222, DexterDay and Russell like this.
  4. Russell

    Russell

    Joined:
    Sep 9, 2015
    Messages:
    1,166
    Likes Received:
    5,631
    Location:
    South Coast , Massachusetts
    Thanks that the info I was looking for I didn't like the idea of the stove constantly turning on and off .
     
    Papelletman and DexterDay like this.
  5. DexterDay

    DexterDay Administrator

    Joined:
    Oct 2, 2013
    Messages:
    12,411
    Likes Received:
    31,636
    Location:
    Northeast Oh
    If it's shutting off and Turing on within 30 min? Then you need a bigger swing/better stat. IMO.

    If it's less than that time? Then it's better to select a lower heat setting and adjust the feed gate to let the stove run constantly. You'll still save more fuel and have a warmer home. In my experience. And my stove is dead center in my ranch (70 ft long).
     
    slvrblkk, Papelletman and Russell like this.
  6. Russell

    Russell

    Joined:
    Sep 9, 2015
    Messages:
    1,166
    Likes Received:
    5,631
    Location:
    South Coast , Massachusetts
    Right now I'm just using it to get the chill out and on the low setting but can already see a thermostat with a swing setting would be the way to go .
     
    slvrblkk, Papelletman and DexterDay like this.
  7. Russell

    Russell

    Joined:
    Sep 9, 2015
    Messages:
    1,166
    Likes Received:
    5,631
    Location:
    South Coast , Massachusetts
    Ok this is the thermostat I went with .If anyone know what wires to use that would be great. My standard CB 1200 thermostat only uses 2 wires. IMG_20150925_122132.jpg
     
  8. Papelletman

    Papelletman

    Joined:
    Sep 10, 2015
    Messages:
    71
    Likes Received:
    343
    Location:
    Plymouth Meeting Pa.
    On my lux I went with the white wire to W1 and red wire to RH, also the Rh is jumped to the RC
     
    Last edited: Sep 25, 2015
    Russell likes this.
  9. Papelletman

    Papelletman

    Joined:
    Sep 10, 2015
    Messages:
    71
    Likes Received:
    343
    Location:
    Plymouth Meeting Pa.
  10. Russell

    Russell

    Joined:
    Sep 9, 2015
    Messages:
    1,166
    Likes Received:
    5,631
    Location:
    South Coast , Massachusetts
    Ok looks easy enough . What's the reason for the jump wire ?
     
  11. Papelletman

    Papelletman

    Joined:
    Sep 10, 2015
    Messages:
    71
    Likes Received:
    343
    Location:
    Plymouth Meeting Pa.
    Comes that way and no reason to remove it.
     
    Russell likes this.
  12. Papelletman

    Papelletman

    Joined:
    Sep 10, 2015
    Messages:
    71
    Likes Received:
    343
    Location:
    Plymouth Meeting Pa.
    RC designated power for cooling, RH for heating.
     
    slvrblkk and Russell like this.
  13. imacman

    imacman

    Joined:
    Oct 23, 2013
    Messages:
    6,630
    Likes Received:
    27,516
    Location:
    Denver, NC
    If you're using the stat just for the pellet stove (heat), you can remove the jumper.
     
    will711, slvrblkk and Russell like this.
  14. Russell

    Russell

    Joined:
    Sep 9, 2015
    Messages:
    1,166
    Likes Received:
    5,631
    Location:
    South Coast , Massachusetts
    Ok all set up let's see what happens. Left jumper on for the moment will that be ok? . IMG_20150925_190553.jpg
     
  15. imacman

    imacman

    Joined:
    Oct 23, 2013
    Messages:
    6,630
    Likes Received:
    27,516
    Location:
    Denver, NC
    Yes. I have the exact stat.....it will still work fine.
     
    Papelletman and Russell like this.
  16. DexterDay

    DexterDay Administrator

    Joined:
    Oct 2, 2013
    Messages:
    12,411
    Likes Received:
    31,636
    Location:
    Northeast Oh
    What's the total swing this unit has Pete? Is it still the large swing if the others in the Lux line up?
     
    Russell likes this.
  17. Russell

    Russell

    Joined:
    Sep 9, 2015
    Messages:
    1,166
    Likes Received:
    5,631
    Location:
    South Coast , Massachusetts
    The swing is 1 - 9 I set it at at 2
     
    Last edited: Sep 25, 2015
  18. Papelletman

    Papelletman

    Joined:
    Sep 10, 2015
    Messages:
    71
    Likes Received:
    343
    Location:
    Plymouth Meeting Pa.
    Number 2 would only be 1/2 a degree swing, if you want a 2 degree swing you need to set it at 8, unless they really changed their thermostats.
     
    Russell likes this.
  19. Russell

    Russell

    Joined:
    Sep 9, 2015
    Messages:
    1,166
    Likes Received:
    5,631
    Location:
    South Coast , Massachusetts
    I'm reading up on that now , you're correct . Thank you I'm getting there .
     
    Papelletman likes this.
  20. DexterDay

    DexterDay Administrator

    Joined:
    Oct 2, 2013
    Messages:
    12,411
    Likes Received:
    31,636
    Location:
    Northeast Oh
    Each one is .25°. So 8 would be 4° total swing.

    2° isn't enough for that type of stove. Having owned one for several years, a hot start is not good on the glass, thermocouple, firebox, etc.

    I'd run 8-9 on the swing. A Quad can be a dangerous stove if the thermocouple doesn't cool enough and the stove restarts. The flame is HUGE and sounds like a freight train.
     
    smoke show, Russell and Papelletman like this.