Discussion in 'Pellet Stoves, Pellet Fireplaces, Pellet Furnaces' started by jtakeman, Jan 21, 2019.

  1. jtakeman

    jtakeman Moderator

    Joined:
    Oct 4, 2013
    Messages:
    12,196
    Likes Received:
    54,983
    Location:
    NW CT foothills
    These freakin power blips/flickers are drivin me nuts(like I needed help)........ Stove restarts, But in low and it goes through a complete start up cycle all over again, Even though it was only off for a breif second or two.

    Looking to tag a UPS on the stove to buffer this issue, But I'd like to add a lil extra feature to trick the stove into not calling for heat and eventually going into shutdown. Pretty sure it only requires a 120 volt relay connected into the stat wire. But could use some assistance on that if anyone has idea's??

    Also could use some assistance with sizing the UPS. I need about 30 minutes of low runtime and about 10 minutes of shutdown(blowers on high and agitator turning to clean burnpot).

    No cash in the kitty, So we'll be waiting until IRS Local goberment returns(if any). Plenty of time to tinker about, wait for a sale and see whats needed. Another note is I usually have 2 or 3 deep cycle marine batteries in the cella October until spring. 2 1000 mah and 1 800 mah. :D
     
  2. badbob

    badbob

    Joined:
    Apr 23, 2014
    Messages:
    2,482
    Likes Received:
    9,946
    Location:
    bozeman pass,park county,MT 6500'
    Harman s have the shutdown feature built into the board,but,even those might restart upon power coming back on,I do not know.I do remember seeing a posting where someone added a timer relay,to do what you want.Will keep in back of mind,when searching for stuff.
     
    ivanhoe, imacman, CleanFire and 2 others like this.
  3. stuckinthemuck

    stuckinthemuck

    Joined:
    Oct 4, 2013
    Messages:
    3,218
    Likes Received:
    15,076
    Location:
    Wandering around in the NH woods.
    Looks like this was just posted a few days ago..

    Battery Backup For Pellet Stoves - 3 Ways To Keep The Heat On

    I was going to suggest getting a 5 amp battery charger, attach it to your batteries which you can connect in parallel and attach a 1000 watt pure sine wave inverter to power the stove. Your manual says the maximum draw is 504 watts. So in theory, the system would work similar to the electrical system in your car... as long as you are charging, you won’t deplete the batteries... when you lose power, you’ll end up on pure battery power until the power is restored or the battery is depleted... could probably come up with a setup for a couple hundred bucks...
     
    ivanhoe, CleanFire and jtakeman like this.
  4. jtakeman

    jtakeman Moderator

    Joined:
    Oct 4, 2013
    Messages:
    12,196
    Likes Received:
    54,983
    Location:
    NW CT foothills
    Thanks, Article should help figure out the UPS capacity!! I also picked up a dohicky that measures power usage at a tag sale this summer. Just need to figure out where I put it!! :emb:

    I've got a 10K house genny for long outages, Its these short blips, Also when I'm not at home and stove just shutting off at a full burn worries.
     
  5. stuckinthemuck

    stuckinthemuck

    Joined:
    Oct 4, 2013
    Messages:
    3,218
    Likes Received:
    15,076
    Location:
    Wandering around in the NH woods.
    With those three batteries hooked up in parallel and a 1000 watt inverter, you should be able to get at least half a day of operations running the stove and maybe more. That’ll help you out if there is an outage while you are away from home as long as you’re coming back the same day. I have a kill-a-watt that you just plug the appliance into to find out how much it draws... you could monitor a cycle from startup to shutdown and see what the average draw is then do some math... you could also test it out while you are home and see just how long one of the batteries lasts... might take a while though... better get some :coldone:

    A quick look at this website shows how to do some calculations... looking at a site that sells deep cycle marine batteries, a group 31 battery has a capacity of 100 amp hours when discharged over 20 hours... so that’s about 5 amps per hour for 20 hours. Your stove, at the maximum, draws 4.2 amps... so one new group 31 battery should last you over 20 hours... you will of course have to subtract some efficiency to convert DC to AC power, but it shouldn’t be too much...

    Let us know what you decide to do..
     
  6. slvrblkk

    slvrblkk

    Joined:
    Oct 6, 2013
    Messages:
    6,647
    Likes Received:
    29,535
    Location:
    Northampton, PA
    Jay...you can also just use a 12 or 24 volt relay and use a small power supply to it...like one for a modem or (wireless) router.
     
  7. CleanFire

    CleanFire

    Joined:
    Aug 28, 2015
    Messages:
    2,997
    Likes Received:
    16,525
    Location:
    .
    We get a solid hour+ of run time out of the Cyberpower 1500 PFC ups unit here JT. Glitches, short outages. etc. are not even a concern - stove doesn't skip a beat. Shutdown cycle here is about 20 mins., ups handles it fine, uses about 25% battery capacity to do, no burn pot agitator though.
     
  8. jtakeman

    jtakeman Moderator

    Joined:
    Oct 4, 2013
    Messages:
    12,196
    Likes Received:
    54,983
    Location:
    NW CT foothills
    Ya ya, Thats the do hicky thing I bought at the tag sale. :)

    A bit under the weather, So I might take tomorrow off and investigate the power requirements. That is If I can find the do hicky thingy..............
     
  9. stuckinthemuck

    stuckinthemuck

    Joined:
    Oct 4, 2013
    Messages:
    3,218
    Likes Received:
    15,076
    Location:
    Wandering around in the NH woods.
    I image your system, on average, doesn’t draw a lot more than a hundred watts or so then. According to their website, if you had a constant draw of 450 watts, you’d be out of power in 11 minutes.

    1500 VA UPS Products | CyberPower

    The graph shows 75 minutes of run time at 100 watts.

    Runtime Calculator | Power Runtime Calculating Tool
     
  10. ivanhoe

    ivanhoe

    Joined:
    Oct 18, 2013
    Messages:
    2,981
    Likes Received:
    11,868
    Location:
    Northern Ontario
    I second this avenue if not longer than a few minutes otherwise you need a longer resource and that's when you start to :emptywallet:
     
    CleanFire, jtakeman and imacman like this.
  11. jtakeman

    jtakeman Moderator

    Joined:
    Oct 4, 2013
    Messages:
    12,196
    Likes Received:
    54,983
    Location:
    NW CT foothills
    UPS sounds like the easy route, But not sure I can get one cheap that will handle the time required for it to run its full 1/2 hour idle and 10 minute shutdown.'

    Looky what I found! :)
    IMG_1135.JPG

    Gonna get the house temp up and shutdown the stove. Get the killa watt dohicky connected and take some readings. I'll do Start up-run-idle and shutdown draws JIC. Although I don't think I'll need the start up as it shouldn't call for heat if I get the relay in the stat circuit to break with no house current.
     
  12. ivanhoe

    ivanhoe

    Joined:
    Oct 18, 2013
    Messages:
    2,981
    Likes Received:
    11,868
    Location:
    Northern Ontario
    The mentioned UPS is to keep going like the [​IMG]and not miss a beat, no shut down required :thumbs:
     
    CleanFire, jtakeman and slvrblkk like this.
  13. slvrblkk

    slvrblkk

    Joined:
    Oct 6, 2013
    Messages:
    6,647
    Likes Received:
    29,535
    Location:
    Northampton, PA
    Jay...you might want to hold out until president's day with the UPS......If memory serves :whistle:, I think they put those on sale at that time at nearly half off.
     
    ivanhoe, CleanFire and jtakeman like this.
  14. jtakeman

    jtakeman Moderator

    Joined:
    Oct 4, 2013
    Messages:
    12,196
    Likes Received:
    54,983
    Location:
    NW CT foothills
    Not sure I can afford one that lasts more than a few hours. Best I opt to shut it down??

    Unless I can stab my deep cycle's unto the UPS?? :whistle:

    :D
     
    ivanhoe, CleanFire and slvrblkk like this.
  15. CleanFire

    CleanFire

    Joined:
    Aug 28, 2015
    Messages:
    2,997
    Likes Received:
    16,525
    Location:
    .
    Eh, "ganging" an Inverter in front of a UPS (regardless of brand), unless the Inverter is a true clean sine-wave unit ($$$) may not work as intended - when I tried this w/ the APC Smart UPS 1350 here back in '15 - it was problematic, at best. The APC unit -did not like- the inverter feed, at all.

    * To be fair, most (older) APC units do not like anything other than utility-grade "clean" power as input, in any case. Our generator here is close enough that it doesn't complain on "low sensitivity" setting, after I tweaked the genny governor to output less than < 61.2 Hz, at 1/2 (2,750w) load.

    re: "roll your own big-azz batteries" on the UPS ( vs. stock ) - unless you have a (separate) charge controller setup, you'll burn up the internal controller circuitry quickly - at least on the modern units, AFAIK.

    To the best of my knowledge, on anything 1,000 watts -> above, (2) Amp Hr. higher vs. installed spec. is the max. you can to go w/ over-sizing batteries on the "consumer" grade units. *That's really the most one can go anyway: the physical dimensions of the battery packs change beyond that / they won't fit.

    An older "Data Center" grade UPS would give you a lot more options to "customize" - the newer UPS units are "down-sized" in circuitry close to the stated spec. - to save weight and install space, to the best of my knowledge.

    Hope this helps JT.
     
    ivanhoe, stuckinthemuck and jtakeman like this.
  16. CleanFire

    CleanFire

    Joined:
    Aug 28, 2015
    Messages:
    2,997
    Likes Received:
    16,525
    Location:
    .
    :coldone: I scored both Cyberpower 1,500 APC :loco: :crazy: PFC units here on those sales, for $120 / each on ...zon Prime, and very grateful to the FHC folks who posted that sale info. up. :yes:
     
    Last edited: Jan 22, 2019
  17. CleanFire

    CleanFire

    Joined:
    Aug 28, 2015
    Messages:
    2,997
    Likes Received:
    16,525
    Location:
    .
    That's very true.

    Cold start: auger only - 78 -> 140 watts,
    Cold start: auger, and igniter: 280 watts -> peaks around 420 watts on auger feed,
    Proof of flame (combustion blower & auger motor) / igniter off: 38 -> 140 watts,
    --
    Running (combustion,convection, auger motor): 27 -> to 140 watts, on auger feed.

    The drop-tube auger feed motor pulls peak about 1/3 way through the auger cycle / as it loads up.

    Shutdown: 35 - 40 watts constant, combustion & convection blowers only.

    Source: Wattage meter display on the Cyberpower UPS unit. ** All values approxmate. Your mileage may vary. Always wear your seat belt. :whistle:
     
  18. jtakeman

    jtakeman Moderator

    Joined:
    Oct 4, 2013
    Messages:
    12,196
    Likes Received:
    54,983
    Location:
    NW CT foothills
    Ugh........ I'z gonna need a big UPS for this beast! :headbang::doh:

    Start up Approx 7 minutes
    watts 458
    VA 486
    AMPS 6.82

    Run medium heat setting
    watts 209
    VA 395
    AMPS 3.11

    Run low heat or maintain mode
    watts 184
    VA 370
    AMPS 2.74

    Shutdown w/ agitator on approx 3 minutes
    watts 182
    VA 328
    AMPS 2.71

    Shutdown w/ agitator off
    watts 153
    VA 271
    AMPS 2.28

    Off to crunch numbers :rolleyes:
     
  19. jtakeman

    jtakeman Moderator

    Joined:
    Oct 4, 2013
    Messages:
    12,196
    Likes Received:
    54,983
    Location:
    NW CT foothills
    Now ya tell me!! o_O
     
  20. slvrblkk

    slvrblkk

    Joined:
    Oct 6, 2013
    Messages:
    6,647
    Likes Received:
    29,535
    Location:
    Northampton, PA
    :thumbs: