Draft Question

Discussion in 'Pellet Stoves, Pellet Fireplaces, Pellet Furnaces' started by Kevin1024, Jan 1, 2017.

Tags:
  1. Lousyweather

    Lousyweather

    Joined:
    Dec 23, 2013
    Messages:
    2,798
    Likes Received:
    9,040
    this is a great thread! all the helpful advice!
    SOOOO many things wrong here with this installation.
    1. I know some will disagree, but WAY too much intake pipe at 3"
    2. Any screen on the intake?
    3. Anything covering the exhaust to keep critters out?
    4. Any blockoff plate, as per the manual?
    5. Had there been a draft test done, I think it would show insufficient combustion air (acutally would show as a high draft on the draft meter, as the intake was restricted)
    6. No tee.....ridiculous with a liner....what if the flyash in the liner avalanches inside?
    7. the flue should be capped with an intake cap....Harman makes one
    8. all that tape...not feeling good about any of the connections near the stove.....ICC has a bolt-on adapter for Harman, a PASH6, as well as a LINER ADAPTER, which could go on right on top of the tee- all gasketed and screwed connections, not requiring tape or silicone....much cleaner
    9. I have no faith in building inspectors......just because they have/had inspected it, it doesn't mean its correct OR safe
    10. If in fact that ell is not pellet vent and is single wall, it should fail an inspection. One cannot simply mix and match pipe to "get it to work". I know this might be unpopular here, but the pipe is UL listed, which is why you can use it. Mix and match? No more UL listing. Single wall pipe is made for negative pressure situations, while pellet pipe is made for positive pressure applicances.....a pellet stove, for instance.
    11. Looks like Simpson pipe......ugh :(
    12. Intake pipe appears crushed at the intake nipple
     
  2. ivanhoe

    ivanhoe

    Joined:
    Oct 18, 2013
    Messages:
    2,981
    Likes Received:
    11,868
    Location:
    Northern Ontario
    Poor Kevin, when people don't know any better sure gets the short end of the stick by those incompetent sellers. I'm sure glad you ventured here for answers for safety sound advice. Just be prepared for a hopefully not too long solving remedy. If you're gonna continue using the unit, I would have a carbon monoxide detector in that room like Cleanfire suggested. I wouldn't tamper too much on the installation as the seller would use that against you. So in the mean time, I will be :popcorn:. Keep us updated on the progress of the situation.
     
  3. SmokeyTheBear

    SmokeyTheBear

    Joined:
    Oct 7, 2013
    Messages:
    8,185
    Likes Received:
    38,844
    Location:
    Standish, ME
    Kevin say hello to Kevin. This is LW he sells those Harman stoves and pellets and installation services. I think he knows what of he speaks.
     
  4. SmokeyTheBear

    SmokeyTheBear

    Joined:
    Oct 7, 2013
    Messages:
    8,185
    Likes Received:
    38,844
    Location:
    Standish, ME
    Preach on brother.
     
  5. Lousyweather

    Lousyweather

    Joined:
    Dec 23, 2013
    Messages:
    2,798
    Likes Received:
    9,040
    'nuff said...I feel bad for Kevin
     
    TBONE, IHATEPROPANE, ivanhoe and 2 others like this.
  6. SmokeyTheBear

    SmokeyTheBear

    Joined:
    Oct 7, 2013
    Messages:
    8,185
    Likes Received:
    38,844
    Location:
    Standish, ME
    You are running like I do now which is poorly, me because I haven't finished my stroke recovery yet you because you don't realize the tiger you have by the tail can leave you stone cold dead.
     
  7. Lousyweather

    Lousyweather

    Joined:
    Dec 23, 2013
    Messages:
    2,798
    Likes Received:
    9,040
    on the positive side, its pretty easy to fix......do a blockoff, get a intake cap, use ICC pipe to make the connection.....an hours work?
     
    IHATEPROPANE, ivanhoe and CleanFire like this.
  8. SmokeyTheBear

    SmokeyTheBear

    Joined:
    Oct 7, 2013
    Messages:
    8,185
    Likes Received:
    38,844
    Location:
    Standish, ME
    Well time to pack it in I have cleaned the stove and taken my #1 favorite pill Flomax .4 mg look it up that is my 2 AM wakeup.
     
  9. Lousyweather

    Lousyweather

    Joined:
    Dec 23, 2013
    Messages:
    2,798
    Likes Received:
    9,040
    .4 mg Tamsulosin here! Once a day
     
    CleanFire, IHATEPROPANE and ivanhoe like this.
  10. SmokeyTheBear

    SmokeyTheBear

    Joined:
    Oct 7, 2013
    Messages:
    8,185
    Likes Received:
    38,844
    Location:
    Standish, ME
    Now you know I can't like that at all. They suck big time.
     
  11. DexterDay

    DexterDay Administrator

    Joined:
    Oct 2, 2013
    Messages:
    12,411
    Likes Received:
    31,632
    Location:
    Northeast Oh
    I read about every other post. But it's all 33 ft? Straight up the chimney? Insulated once it's above the lentil? Or no? I see no block off as mentioned ealrier. That's a big problem.

    Insulated will help as well as what STB and LW said.
     
  12. savemoney

    savemoney

    Joined:
    Oct 3, 2013
    Messages:
    13,470
    Likes Received:
    69,188
    Location:
    Chelsea Maine
    Omg. I'm glad I waited to read all this first. Smokey is right. That set up is so blundered. I hate to admit it but I paid over 900 for a simple t and three feet up and out. Put the OAK in myself. That was on my fist stove in 2008. The installer made a bunch of mistakes. Smokey was the one who had patience with me and helped me get it right. Lots of others sounded in with their support. Jay and Dexter helped me select my second day stove. This is the right place to be to work out burning issues.
     
  13. DexterDay

    DexterDay Administrator

    Joined:
    Oct 2, 2013
    Messages:
    12,411
    Likes Received:
    31,632
    Location:
    Northeast Oh
    You still treated that Napoleon right. When it was clean and running a good pellet it ran good (good enough). But a better stove that can burn anything helps a lot. Along with a proper OAK setup. Glad you finally got that Harman!

    That 3" OAK he has that is 33 ft long? Probably a bit much for that diameter.
     
  14. Kevin1024

    Kevin1024

    Joined:
    Nov 27, 2016
    Messages:
    55
    Likes Received:
    184
    Location:
    Nj
    All they did was stuff insulation up the chimney after the piping went up.
     
  15. Kevin1024

    Kevin1024

    Joined:
    Nov 27, 2016
    Messages:
    55
    Likes Received:
    184
    Location:
    Nj
    I think you guys are right. That OAK run is 33 ft straight up the chimney and out with 3 inch pipe. And it was crimped a bit toward the stove. No other OAK install options so my gut tells me to live without it since my stove is running flawlessly now. I've reached out to my installer to let him know I have some leakage. If I don't hear back from him, I'm calling the inspector to come out.
     
    CleanFire, ivanhoe, Rich250 and 2 others like this.
  16. stuckinthemuck

    stuckinthemuck

    Joined:
    Oct 4, 2013
    Messages:
    3,218
    Likes Received:
    15,076
    Location:
    Wandering around in the NH woods.
    Do you have a basement or a crawl space? Could you go down through the hearth pad and out the side of the house like a dryer vent? Obviously just conceptual and not installation advice.. I'll defer to the experts for that..
     
    CleanFire, ivanhoe and IHATEPROPANE like this.
  17. Lousyweather

    Lousyweather

    Joined:
    Dec 23, 2013
    Messages:
    2,798
    Likes Received:
    9,040
    some OAK install options? Yea there is. Use a short section of UNcrimped intake pipe, run it from the intake nipple on the P68 up through the block-off plate (which isn't there), extend a few feet above it (total length 5-6'), terminate the 4" liner (at the top of the chimney) with the correct cover plate (this suspends the liner and closes off the flue pipe from the elements), and the cover plate sits on the Harman SS top intake, #1-00-674104. Easy Peezy.

    I would like to point out here, not to hijack the thread, that in another post on this site, folks seemed to think a 3" intake pipe was adequate to pull air from the top of the chimney....I disagreed, and here is proof that I am......, well, never mind........
     
    DexterDay, CleanFire, ivanhoe and 2 others like this.
  18. Lousyweather

    Lousyweather

    Joined:
    Dec 23, 2013
    Messages:
    2,798
    Likes Received:
    9,040
    good idea, doesnt look great though
     
    CleanFire, ivanhoe and IHATEPROPANE like this.
  19. CleanFire

    CleanFire

    Joined:
    Aug 28, 2015
    Messages:
    2,997
    Likes Received:
    16,525
    Location:
    .
    LW, this would suspend the OAK inlet inside the chimney (above the smoke shelf), the venting would still be terminated at the top of the chimney (using the correct method), the cover plate on top will have an air opening for the OAK inlet feed inside the chimney space?
     
    ivanhoe, Lousyweather and Rich250 like this.
  20. Kevin1024

    Kevin1024

    Joined:
    Nov 27, 2016
    Messages:
    55
    Likes Received:
    184
    Location:
    Nj
    Will do. Ok. So if an inspector comes and sees the smoke leakage at start up, will he enforce a "t" be installed or would he allow the existing set up with silicone to stop the leak if in fact that works? And if a "t" is required or whatever else, is it on the installer to pay for it all?
     
    CleanFire and ivanhoe like this.