woodstock IS and chimney

Discussion in 'Modern EPA Stoves and Fireplaces' started by chucker, Sep 8, 2016.

  1. chucker

    chucker

    Joined:
    Apr 14, 2015
    Messages:
    134
    Likes Received:
    289
    Location:
    New York
    pic of new chimney setup. it was 3' shorter last year and performance was not good from the IS. there was 9'4" of inside + outside pipe and the stove worked although i didn't use it with catalyst engaged. i had a crisis where i was sole caregiver to a family member, had my hands full, and didn't want to get in a position where i could have any type of accident.
    the chimney is 8" metalbestos which i blacked out with SEM automotive trim paint. its claim to fame is neat low luster finish and good adherence to chrome and stainless steel. the black goes nicely and is more understated than if it were shiny, and won't show smoke or creosote stain the same way. the length is now 12'4" which i hope is enough. i am in new york and won't have to run the stove until later this month. the pipe is now about 6' off the roof, just under that. i put an aluminum wedge into the roof flashing which has 3 u-channels riveted in and the pipe gets some support at each evenly spaced u-channel from that point at the top of the flashing which is about 6" above the shingles. if possible it can stay that way without a roof bracket. should it need a roof bracket it will get attached to the ridge, a spot which never gives you fits and can't leak much if at all. old carpenters like me avoid problems before they start. we understand murphy's law.
    first of all my wood was not 3 years old last winter, the chimney wasn't long enough, and the stove worked but did not get hot enough to cook on. it did well though with only secondary combustion and in that mode made far fewer ashes than the jotul 500 it replaced. i look forward to this winter, wood is now 2 years old and pretty dry. i don't have the 15' of stack they recommend and hope to get by as is.
     

    Attached Files:

    • 001.JPG
      001.JPG
      File size:
      723.7 KB
      Views:
      53
  2. HarvestMan

    HarvestMan

    Joined:
    Feb 22, 2015
    Messages:
    744
    Likes Received:
    3,272
    Location:
    Southeastern Michigan
    Sorry, but this is not adding up for me. Why not install the extra 3 feet of pipe and roof support?
     
  3. Babaganoosh

    Babaganoosh

    Joined:
    Sep 7, 2015
    Messages:
    1,137
    Likes Received:
    3,827
    Location:
    Jersey Shore
    I have the same length of pipe and chimney. 12 foot. It will probably work fine when it's cold. You will really appreciate the extra length in the shoulder season when you would be struggling with good draft. The extra draft will allow you to burn lower and slower during those times. If you can get the extra few feet go for it. If not you will be ok.
     
  4. chucker

    chucker

    Joined:
    Apr 14, 2015
    Messages:
    134
    Likes Received:
    289
    Location:
    New York
    it would be easier if the chimney was further up the roof toward the ridge. adding the extra 3' of pipe would make the cap over 9' from the shingles and extremely difficult to service. as it is right now i can put my hands on it standing on the roof. it would also look ungainly. push come to shove i will have to add the extra 3'. the roof support is no thing of beauty either.
     
    My IS heats my home likes this.
  5. Canadian border VT

    Canadian border VT

    Joined:
    Feb 18, 2015
    Messages:
    18,256
    Likes Received:
    119,597
    Location:
    Vermont
    if you put support right below last 3 foot piece.. the top piece you just pull off with screen clean screen. height is basically same as now.. That IS will amaze you once you use the cat! trust me!
     
    bobdog2o02 and Backwoods Savage like this.
  6. chucker

    chucker

    Joined:
    Apr 14, 2015
    Messages:
    134
    Likes Received:
    289
    Location:
    New York
    thanks, lucid explanation. i'm wondering if a short, hot fire will suffice in the shoulder season and carry the house through the day. it won't be a mystery much longer as it looks like the first burn will be in about a week. the most important time for a slow burn is in the dead of winter when fuel consumption can add up. i'll keep my eye on it. maybe the stack can be lengthened another 2' if necessary for a total of 14'4".
     
    Backwoods Savage likes this.
  7. My IS heats my home

    My IS heats my home

    Joined:
    Dec 1, 2013
    Messages:
    7,394
    Likes Received:
    17,655
    Location:
    Albany, NH
    So much in common with chucker , we are both carpenters, we both know Murphy and his dastardly ways and we both owned a Jotul Oslo prior to the IS. Small world.

    I agree with the fellas, too bad you couldn't get that flue just a bit higher to increase your draft. Do you have a prevailing wind thats fairly regular? As Canadian border VT was saying, if you put the last section on to what you have now you can always remove it for cleaning at a manageable height and replace it when your done.

    Since you didn't have entirely dry wood last season and did not use the cat much, what did your flue produce when you did your cleaning?
     
    Backwoods Savage likes this.
  8. Babaganoosh

    Babaganoosh

    Joined:
    Sep 7, 2015
    Messages:
    1,137
    Likes Received:
    3,827
    Location:
    Jersey Shore
    The IS really wasn't really designed for a hot quick fire. I mean you can do it but it's not it's strength.
     
  9. My IS heats my home

    My IS heats my home

    Joined:
    Dec 1, 2013
    Messages:
    7,394
    Likes Received:
    17,655
    Location:
    Albany, NH
    +1, 100% agree
     
  10. Backwoods Savage

    Backwoods Savage Moderator

    Joined:
    Oct 4, 2013
    Messages:
    46,966
    Likes Received:
    295,816
    Location:
    Central MI
    I might be guessing here but it seems to me your biggest problem is the 8" vs 6" chimney rather than the height. Height still can be a problem but 8" vs 6" can and will cause big problems when a stove is designed to be used with 6".

    I also agree that you can always remove the top section of chimney for cleaning then replace it without much work at all.

    I also really can not see any sense in not running the cat when the stove is designed to be used with a cat.

    You may not have to run that stove later this month if this weather doesn't change drastically soon. Right now I'm sort of betting we may not have a fire until into October this year. Time will tell on that one.
     
  11. My IS heats my home

    My IS heats my home

    Joined:
    Dec 1, 2013
    Messages:
    7,394
    Likes Received:
    17,655
    Location:
    Albany, NH
    I didn't see the 8" part, thats a cause for concern. WS IS suggests (requires?) 6"
     
    Backwoods Savage likes this.
  12. chucker

    chucker

    Joined:
    Apr 14, 2015
    Messages:
    134
    Likes Received:
    289
    Location:
    New York
    dennis

    i was given to believe that people vented their IS into masonry chimneys where the tile liners have more area than 8" round pipe, and that was an acceptable setup. what is the basic problem with 8" pipe?
    it wouldn't be much trouble to put a 6" liner into the pipe. would this improve things greatly?
     
    Backwoods Savage likes this.
  13. chucker

    chucker

    Joined:
    Apr 14, 2015
    Messages:
    134
    Likes Received:
    289
    Location:
    New York
    tell you what i am mostly a cabinetmaker now and it would take a few weeks in the field to be an acceptable carpenter again. i love the shop work. it's an entire study setting up a shop and getting into factory science.
    i cleaned the stove a few times last winter. we have a slip pipe where you can take out a screw, remove the couple sections of pipe, and then clean the stack with a couple of rods and a brush from inside the house. the wood had been cut earlier in the year and gone through the summer and then been covered. the entire winter produced about 5 gallons of creosote, certainly no more than 10.
    i am looking at pipe sections now and appreciate your feedback. an 18" section would get me to 13'10" and i would still just be able to stand on the roof and remove the cap, and it would probably present an acceptable appearance, and a good chance on getting away without bracing. interesting study, this little bit.
     
  14. brenndatomu

    brenndatomu

    Joined:
    May 29, 2015
    Messages:
    23,442
    Likes Received:
    150,627
    Location:
    NE Ohio
    It would, almost half the area...28 VS 50 sq. in.
     
    Backwoods Savage likes this.
  15. saskwoodburner

    saskwoodburner

    Joined:
    Dec 15, 2015
    Messages:
    2,610
    Likes Received:
    14,874
    Location:
    middle of nowhere Saskatchewan, Canada
  16. brenndatomu

    brenndatomu

    Joined:
    May 29, 2015
    Messages:
    23,442
    Likes Received:
    150,627
    Location:
    NE Ohio
    After looking at your pic again...thats 8"? Looks like 6" pipe...is it 8" OD?
    That would give you 6" ID on a class A pipe, which is correct then
     
  17. brenndatomu

    brenndatomu

    Joined:
    May 29, 2015
    Messages:
    23,442
    Likes Received:
    150,627
    Location:
    NE Ohio
    I like to use this simple formula to find area of a circle. Diameter X Diameter X .785 = area.
    Then you can multiply area X height to get cylinder volume if you want that.
     
  18. chucker

    chucker

    Joined:
    Apr 14, 2015
    Messages:
    134
    Likes Received:
    289
    Location:
    New York
    it's 8" metalbestos pipe, i guess selkirk pipe now, so it's 10" OD. it's hard to see proportion in the picture. i checked the online manual for the IS, they are okay with 8" square flue as an exterior setup, and maximum 8" round pipe, again as an exterior chimney. i don't doubt that 6" draws somewhat better. the 8" pipe got installed in the house decades ago when we had a vermont castings defiant that vented with 8" pipe. it was a big deal in those days to have an airtight stove. things have progressed.
     
  19. Babaganoosh

    Babaganoosh

    Joined:
    Sep 7, 2015
    Messages:
    1,137
    Likes Received:
    3,827
    Location:
    Jersey Shore
    5 gallons? Wow. My IS had about one cup of ash and creosote and I didn't even have perfect wood yet. This year I will though.

    Run that cat!
     
  20. TurboDiesel

    TurboDiesel

    Joined:
    Nov 22, 2013
    Messages:
    16,196
    Likes Received:
    97,190
    Location:
    Hollidaysburg Pa
    This is not good, chucker.
    The IS shouldn't make 5-10 cups of dust in a year in 14 feet of pipe.
    you need to engage the cat...and you already know seasoning wood for 1-3 years is the key

    Engaging the cat will bring the firebox temp up and make it efficient, and lower the flue temp at the same time.