Propane Question

Discussion in 'The DIY Room' started by eatonpcat, Jun 14, 2016.

  1. eatonpcat

    eatonpcat

    Joined:
    Oct 5, 2013
    Messages:
    9,694
    Likes Received:
    54,102
    Location:
    Eaton Township, OH
    Generac 12KW Standby Generator (LP)

    13 years old and the motor threw a rod, so it is toast. Going to replace it and I am trying to figure out if my gas line supplies enough LP to run a new 20KW unit.

    I posted this on another forum and got no good answer, so I figure maybe someone at FHC could help.

    If this table is correct, it looks like my 1" gas pipe should run a 20kw (200,000 btu), my furnace (90,000 btu) and gas cooktop (45,000 btu). Any disagreement??

    But it looks like I will be getting 480,000 btu's from a 1" diameter pipe with a 50 foot run
     

    Attached Files:

  2. ironpony

    ironpony

    Joined:
    Oct 4, 2013
    Messages:
    3,564
    Likes Received:
    18,715
    Location:
    Mid Ohio

    Agree and you appear to have quite a buffer, also all the appliances will not be running full tilt at the same time

    Do you have one inch from the service to the generator directly with half-inch feeds to the appliances?

    That is probably for the mainline and then usually half inch branches to all the appliances
     
  3. intheBigWoods

    intheBigWoods

    Joined:
    Dec 27, 2015
    Messages:
    72
    Likes Received:
    571
    Location:
    central North Carolina
    Side note: you might want to consider the Generac 22kw rather than the 20, the larger one is a newer design and burns less propane than the 20. I installed the 22kw propane Generac last year and I am very happy with it.
     
  4. eatonpcat

    eatonpcat

    Joined:
    Oct 5, 2013
    Messages:
    9,694
    Likes Received:
    54,102
    Location:
    Eaton Township, OH
     
  5. eatonpcat

    eatonpcat

    Joined:
    Oct 5, 2013
    Messages:
    9,694
    Likes Received:
    54,102
    Location:
    Eaton Township, OH

    The 20KW is on sale for 500.00 off, I believe because it is being replaced by the 22KW. Thanks for your input.
     
  6. ironpony

    ironpony

    Joined:
    Oct 4, 2013
    Messages:
    3,564
    Likes Received:
    18,715
    Location:
    Mid Ohio
    so what size is the line supplying the generator now?
    the 1 inch line is plenty big, depending on the length of run you may have to resize the generator feed
     
  7. eatonpcat

    eatonpcat

    Joined:
    Oct 5, 2013
    Messages:
    9,694
    Likes Received:
    54,102
    Location:
    Eaton Township, OH
    It's 1" feeding the generator...I put in the larger line for the first Genny. Sounds like I should be good.

    Thanks for your input IP!!