    Hey, I am playing catch up. I can't believe your still getting blockage out of the furnace. Your flame pic looks great, looks like it should be a hot fire.
    Yes your right about level 1 being draft trim, just not sure if it will fix the dirty glass since the burn is excellent. Not going to adjust it if it's not worth it. I clean the glass every week when I vacuum the furnace. I have gone 2 weeks without vacuuming but prefer good maintenance practice.
     
    CleanFire, BAN83 and ivanhoe like this.
  2. ivanhoe

    ivanhoe

    Joined:
    Oct 18, 2013
    Messages:
    2,980
    Likes Received:
    11,868
    Location:
    Northern Ontario
    A little off topic, can the distribution fan motor be lubricated? Haven't seen any oil ports!
     
    CleanFire and BAN83 like this.
  3. BAN83

    BAN83

    Joined:
    Sep 16, 2015
    Messages:
    400
    Likes Received:
    819
    Location:
    Ontario, Canada
    Have to give the other guys a shake and get them to chime in.

    Yes, those two holes are what I am thinking of blocking. BUT, only on the back plate part, so the air would still be able to get to the main channel of these two holes via up through the bottom of the back plate and down through the top of the back plate. The thought is I'd draw more hot air over the heat exchanger tubes. Please note, I would not block these holes completely, maybe 25%.
     
    CleanFire and ivanhoe like this.
  4. BAN83

    BAN83

    Joined:
    Sep 16, 2015
    Messages:
    400
    Likes Received:
    819
    Location:
    Ontario, Canada
    I'll be honest, I really didn't think I'd find more crap back behind that plate. But I cleaned it again as everyone was very adamant that it must be blocked. Well, jokes on me, there was more debris. All I can figure is the heat got it to come loose during one of the test burns.

    Yeah, the flame is looking much better. Still lacking some heat from the distribution blower, but I'm making headway.

    Let me know how you make out with you settings on heat level 1 and getting it to burn clean. I'll have to go through the same issues once I get there.
     
    CleanFire and ivanhoe like this.
  5. BAN83

    BAN83

    Joined:
    Sep 16, 2015
    Messages:
    400
    Likes Received:
    819
    Location:
    Ontario, Canada
    I have done it in the past on motors but in my experience, if there aren't any oil ports, most of the oil doesn't get where it needs to be. That being said, if you can pull the motor and stand it in such a was as to allow the oil to run into the bearings, you may be able to do it.
     
    CleanFire and ivanhoe like this.
  6. DexterDay

    DexterDay Administrator

    Joined:
    Oct 2, 2013
    Messages:
    12,411
    Likes Received:
    31,628
    Location:
    Northeast Oh
    Yes. There is oil ports on the distribution blower, but it needs removed. As the holes are on the bottom. I only do this every 2 years. It's quite the undertaking.

    Because the area in front of the burn pot is open, there will always be air that goes down. The ash pan has gaps on the side, so air can go down as well. Remember, the distribution blower blows 50% through the exchange tubes. The other 50% is blown around the sides of the firebox and what comes out the bottom slot (I flipped the bottom deflector).

    If you restrict those ports, it will be just like closing the intake damper.

    You'll never get 100% of the air to go down, but the flame is the heat that "rises" and heats the tubes. But that is only a percentage of your heat
     
    CleanFire, BAN83 and ivanhoe like this.
  7. DexterDay

    DexterDay Administrator

    Joined:
    Oct 2, 2013
    Messages:
    12,411
    Likes Received:
    31,628
    Location:
    Northeast Oh
    If you ever remove the distribution blower and it's housing? You'll get a better perspective of where that air is blown.
     
    CleanFire, BAN83 and ivanhoe like this.
  8. ivanhoe

    ivanhoe

    Joined:
    Oct 18, 2013
    Messages:
    2,980
    Likes Received:
    11,868
    Location:
    Northern Ontario
    If you block those holes 100% it will probably do nothing. It might channel it's way to the bottom opening unless it's still blocked :eek:
    Better not be:picard:
     
    CleanFire and BAN83 like this.
  9. ivanhoe

    ivanhoe

    Joined:
    Oct 18, 2013
    Messages:
    2,980
    Likes Received:
    11,868
    Location:
    Northern Ontario
    That's good to know. Can the motor be rotated to the top for easy access? I will look into it further while it's diwn for a rest, pending on weather.
     
    CleanFire and BAN83 like this.
  10. BAN83

    BAN83

    Joined:
    Sep 16, 2015
    Messages:
    400
    Likes Received:
    819
    Location:
    Ontario, Canada

    Good to hear there are oil ports for the distribution motor. Might pull it and oil it then. I've been trying to see the air path and it's hard to get the full picture, so you make a good point that having it out will allow me a better idea of the air path.
     
    CleanFire and ivanhoe like this.
  11. BAN83

    BAN83

    Joined:
    Sep 16, 2015
    Messages:
    400
    Likes Received:
    819
    Location:
    Ontario, Canada
    That's why I was thinking of only closing them of a small percentage.
     
    CleanFire and ivanhoe like this.
  12. ivanhoe

    ivanhoe

    Joined:
    Oct 18, 2013
    Messages:
    2,980
    Likes Received:
    11,868
    Location:
    Northern Ontario
    Do it with the smoke test. And if you can remove the ash pan to better see where it's going. Just put a plexiglass in front of ash pan door opening while you have no heat in there.
     
    CleanFire and BAN83 like this.
  13. ivanhoe

    ivanhoe

    Joined:
    Oct 18, 2013
    Messages:
    2,980
    Likes Received:
    11,868
    Location:
    Northern Ontario
    Air path if I remember is split in two channels.
     
    CleanFire and BAN83 like this.
  14. BAN83

    BAN83

    Joined:
    Sep 16, 2015
    Messages:
    400
    Likes Received:
    819
    Location:
    Ontario, Canada
    That was my concern in doing it, that it would restrict air and put me back into a vey dirty burn.

    I understand that the exchangers are only 50% of my heat, but they seem more like 80% of the heat right now. I don't find that there is any heat coming off the channels that run up the side of the firebox. Have you ever checked this air? To see how hot that portion gets?

    I remember you flipped that bottom deflector in the front. My buddy and I played around with it on Saturday, and we actually added in a piece of a tine to the door that helps deflect the air up the face of the fire box until I can get the deflector mounted.

    Oh well. It was just a thought to try and push more heat through the exchanger tubes. Back to cleaning after training!
     
    Last edited: Dec 15, 2015
    CleanFire and ivanhoe like this.
  15. ivanhoe

    ivanhoe

    Joined:
    Oct 18, 2013
    Messages:
    2,980
    Likes Received:
    11,868
    Location:
    Northern Ontario
    Are you having a hard time getting into the back panel to clean? You're not the only one:confused: You have to think out loud to find useful fabricated tools. If you can get hold of a 3/8" towing stranded wire about 2-3' and make the end strands coming undone like a bad hair day. You can push it up/down or even attach it to a drill and go to town, The right side of the back panel has to be cleaned also but it's a smaller channel. Like I said, you have to be creative to make tools that works around the back panel and hex tubes, etc.., Good time to put the beer to work:drunk:
     
    CleanFire and BAN83 like this.
  16. DexterDay

    DexterDay Administrator

    Joined:
    Oct 2, 2013
    Messages:
    12,411
    Likes Received:
    31,628
    Location:
    Northeast Oh
    The air path will never be 100% down the back. Because the stove draws the air through the bottom 2 holes, it's going to take the path of least resistance. So it's gonna go in front of the pot, through the cracks in the side ash plates, and down the back channel.

    The biggest thing here, is heat rises, so while the smoke pattern may have some air going down the front, the flame is throwing heat up in the exchanger area and that back panel allows for that heat to be brought back down, and pushed out to the back cleanout, then to the blower.

    I think your lack of heat is due to lack of air still. Sounds like you still have a big leak somewhere. Did you double check the ash pan gasket with the dollar test? Hopper leak? Any of the screws going to the firebox with a bad seal. Almost every screw in the front of the firebox goes into the firebox. If they are not tight, air will leak.
     
    CleanFire, ivanhoe and BAN83 like this.
  17. BAN83

    BAN83

    Joined:
    Sep 16, 2015
    Messages:
    400
    Likes Received:
    819
    Location:
    Ontario, Canada
    Using braided steel cable is a great idea!. I actually used a chunck of BX cable and buggered up the outer jacket to make a cleaning tool. I'll try a piece of cable though. I think it will work better. Thanks!
     
    CleanFire and ivanhoe like this.
  18. BAN83

    BAN83

    Joined:
    Sep 16, 2015
    Messages:
    400
    Likes Received:
    819
    Location:
    Ontario, Canada
    True, as much as I try, the air will always take the path of least resistance. I guess I am over htinking this.

    You make a great point about the screws though. They never even entered my mind as a potential spot that the stove may be leaking. I'll have to smoke test the WHOLE stove again when I get home.

    As for the ash pan, I didn't dollar bill test it, but I did smoke test it and there were no signs of leakage. What test do you put more faith in for being the best test of leakage?

    I have room in the damper that I can open it more to create a hotter fire, maybe this is what I need to do. As I said, I'll have to rest the heat outputs when I get home and check with the anemometer I orered, which should arrive while I am away.
     
    CleanFire and ivanhoe like this.
  19. DexterDay

    DexterDay Administrator

    Joined:
    Oct 2, 2013
    Messages:
    12,411
    Likes Received:
    31,628
    Location:
    Northeast Oh
    Your stove is a negative pressure vessel. The exhaust is positive pressure (where you woild see smoke if there was no seal).

    Even if half the ash pan gasket was removed. . No smoke would spill in the room, because it's being sucked "in" through the gap. You'll never know if you have a failing gasket unless you know how tight it seals.

    I should have recorded my entire start up. I thought ignition would be longer.

    I had smoke in under one minute (I started timer as soon as cleaning was done and air pump started). Sparks at around 1:20 seconds and full ignition in 2:30. That's when I started recording so you can see the amount of air flow and sparks (the more air, the more sparks).

    Also, you can see my entire firebox is grey (except where the ash doesn't go/I painted the firebox this year, so any black you see is still paint).

    Video is uploading now. I'll post it shortly after I eat dinner.
     
    CleanFire, BAN83 and ivanhoe like this.
  20. DexterDay

    DexterDay Administrator

    Joined:
    Oct 2, 2013
    Messages:
    12,411
    Likes Received:
    31,628
    Location:
    Northeast Oh
    Or are you implying smoke on the outside? And you're looking for it to suck in?

    I'd still want to know how tight the seal of the gasket is. You may not see the leak if it's small enough. But of that dollar pulls out easily? I'd be replacing the gasket. Even if smoke isn't being pulled in.
     
    ivanhoe, CleanFire and BAN83 like this.