    Okay. My neighbor is having some kind of problem with his new boiler. Same plumbing as before- just attached at the boiler.

    At the furnace plenum, intake and outgo pipes are good and hot, but when the furnace fan is on, there is a significant temperature drop on the return line. Of course it doesn’t warm the house either.

    thoughts? He is pretty handy, and installed his complete boiler before. Frustrated with it
     
  2. Jeffrey Svoboda

    Jeffrey Svoboda

    Joined:
    Sep 28, 2015
    Messages:
    1,374
    Likes Received:
    6,457
    Location:
    Michigan
    Random guess; circulation pump for the water is too slow. Not moving enough water before the furnace fan strips the heat in the heat exchanger?

    I would think the furnace fan and heat exchanger should already be match together.
     
  3. Sourwood

    Sourwood

    Joined:
    Jan 4, 2018
    Messages:
    1,733
    Likes Received:
    13,087
    Location:
    Popcorn, IN
    Jeffrey Svoboda yes the fan exchange been matched for ten years. I think he is using the same Taco pump from the previous boiler.
     
  4. Jeffrey Svoboda

    Jeffrey Svoboda

    Joined:
    Sep 28, 2015
    Messages:
    1,374
    Likes Received:
    6,457
    Location:
    Michigan
    Possibly a partially plugged heat exchanger in the furnace?
     
  5. lukem

    lukem

    Joined:
    Oct 4, 2013
    Messages:
    11,155
    Likes Received:
    57,601
    Location:
    IN
    Sounds like low flow on the line set from the boiler to the water to air heat exchanger. Could be the pump or the heat exchanger.
     
    morningwood and stuckinthemuck like this.
  6. MikeInMa

    MikeInMa

    Joined:
    Dec 4, 2016
    Messages:
    12,130
    Likes Received:
    86,327
    Location:
    Southern Worcester county
    Confused here.

    My understanding is a furnace is used for forced hot air, which we have. A boiler is for baseboard heating.

    I've not heard of a boiler with a fan. I'm probably displaying my ignorance in such matters.
     
    stuckinthemuck likes this.
  7. stuckinthemuck

    stuckinthemuck

    Joined:
    Oct 4, 2013
    Messages:
    3,089
    Likes Received:
    14,319
    Location:
    Wandering around in the NH woods.
    Seems like primary heat source is forced hot air. Boiler is rigged up to provide hot water to heat exchanger at furnace plenum so HVAC can distribute hot air. I would also think low flow to heat exchanger. What kind of boiler is the new boiler? What was in there before? What is the temp as the water enters and exits the heat exchanger?
     
    MikeInMa likes this.
  8. plcnut

    plcnut

    Joined:
    Jan 10, 2016
    Messages:
    10
    Likes Received:
    22
    Location:
    SW Missouri USA
    The issue sounds like low flow to me. The return water is so cool because there is too little water flowing through the exchanger, therefore the temperature delta of the exchanger is very high.
    A plugged exchanger is possible, but does not make sense if his old boiler did not have the same problem.
    Air lock sounds like a likely problem.
    Is it plumbed in a way that he can do a power flush?
     
    Jeffrey Svoboda and morningwood like this.
  9. Sourwood

    Sourwood

    Joined:
    Jan 4, 2018
    Messages:
    1,733
    Likes Received:
    13,087
    Location:
    Popcorn, IN
    MikeInMa No, outdoor boilers operate on forced air heaters. No need to go into further details at the moment..

    plcnut No idea on a powerflush. He replaced his Classic with an EZ All system was operating fine before, Just attached existing plumbing to the new boiler


    Now my boiler pump is out for the third time since December. Tech is coming again. He is wondering if there is a restriction somewhere. It heats fine and then it’s out
     
    MikeInMa likes this.
  10. plcnut

    plcnut

    Joined:
    Jan 10, 2016
    Messages:
    10
    Likes Received:
    22
    Location:
    SW Missouri USA
    What brand of pump are you running?
    Is in mounted correctly?
    What is going bad when it dies? Windings? seals/bearings?
     
  11. morningwood

    morningwood

    Joined:
    Oct 17, 2022
    Messages:
    234
    Likes Received:
    927
    Location:
    Ohio
    He probably has an air lock in his heat exchanger. I put a T in my basement so I can push all of the air in the lines out to the boiler via domestic water pressure.

    Hopefully his circulator is on his boiler and not in the basement. If it is, that's a whole other can of worms.
     
    plcnut and Sourwood like this.
  12. Sourwood

    Sourwood

    Joined:
    Jan 4, 2018
    Messages:
    1,733
    Likes Received:
    13,087
    Location:
    Popcorn, IN
    T is a Taco. The first one went out after 8 years . The replacement was running slow and making a louder noise than normal. They replaced the cartridge u der warranty.

    This time it was making no noise. The tech replaced it with a different model Taco .

    there were no problems with heat performance so no restrictions are overworking the pump
     
    plcnut likes this.
  13. brenndatomu

    brenndatomu

    Joined:
    May 29, 2015
    Messages:
    20,531
    Likes Received:
    127,900
    Location:
    NE Ohio
    Bingo.
    What is the temp differential before n after the HX?
     
    morningwood and plcnut like this.
  14. plcnut

    plcnut

    Joined:
    Jan 10, 2016
    Messages:
    10
    Likes Received:
    22
    Location:
    SW Missouri USA
    I have been happy with Taco pumps.
    Your last failure sounds like a winding problem. Most other failures lead to excess noise.
    Hopefully you are just dealing with faulty parts and your new pump will last.

    I do know that if the shaft is not horizontal you are likely to have issues.
    Also, if the flow through your pump is down, then you need to take extra precautions to ensure no air gets to the pump. When pumping downhill then air bubbles can sit in the pump and slow the flow which can lead to overheating of the pump. I prefer for flow to be up whenever possible so that any air in the system will flow past the impeller.
     
    brenndatomu likes this.
  15. morningwood

    morningwood

    Joined:
    Oct 17, 2022
    Messages:
    234
    Likes Received:
    927
    Location:
    Ohio
    Depending on pump speed, I see about 15 - 20F across the HX in my furnace. I'd expect the OP to see something similar.
     
    brenndatomu likes this.
  16. brenndatomu

    brenndatomu

    Joined:
    May 29, 2015
    Messages:
    20,531
    Likes Received:
    127,900
    Location:
    NE Ohio
    Not apples to apples by any means, but the boiler at work drops about 40* across the HX.
     
    morningwood likes this.
  17. morningwood

    morningwood

    Joined:
    Oct 17, 2022
    Messages:
    234
    Likes Received:
    927
    Location:
    Ohio
    Any idea on how many GPM's ? That's a serious amount of heat loss. My guess is, easily >100k BTU's.
     
    brenndatomu likes this.
  18. brenndatomu

    brenndatomu

    Joined:
    May 29, 2015
    Messages:
    20,531
    Likes Received:
    127,900
    Location:
    NE Ohio
    I'd have to look up the pump rating...the boiler is rated at 600k BTU, but we have the burner turned down.
     
    morningwood likes this.
  19. yooperdave

    yooperdave

    Joined:
    Jun 16, 2014
    Messages:
    32,086
    Likes Received:
    194,417
    Location:
    Michigan's U.P.
    We are dealing with 1" lines all throughout the system I hope? Sometimes, a DIY will buy a less expensive heat exchanger with smaller than 1" connectors.

    Also, I think you mentioned that the heat exchanger is sized (btu output) for the house also? Can't remember
     
    brenndatomu likes this.
  20. brenndatomu

    brenndatomu

    Joined:
    May 29, 2015
    Messages:
    20,531
    Likes Received:
    127,900
    Location:
    NE Ohio
    Only thing that has changed from before (when it worked) is the boiler itself...I still say there's air in it