    A friend of mine is replacing an old smoke dragon with an NC 30. Interior is 8" single wall up, about 8'. Exterior is 8" class A, 'bout 12' -so 20' total rise, straight up.
    Looking for the least expensive way to vent the NC30.
    Can a 6" liner fit down through the 8" Class A? or...
    Run new 6" single or double wall to a 6"-8" adapter connected to the existing 8" Class A? Not my choice.
    What do you think? Looking for options. Thanks, JB
     
    wildwest likes this.
  2. papadave

    papadave

    Joined:
    Oct 3, 2013
    Messages:
    18,181
    Likes Received:
    82,470
    Location:
    Right where I want to be.
    I'd try the 6" stove pipe to the increaser route. If it doesn't draw well, then revisit the issue.
     
  3. Beetle-Kill

    Beetle-Kill

    Joined:
    Nov 23, 2013
    Messages:
    4,102
    Likes Received:
    19,559
    Location:
    Near the Divide, Colorado
    Guess I'll recommend the increaser, see what happens. Now, dbl. or single wall for the interior? He has no clearance issues so single would work fine.
    I'm just concerned about accumulation in the 8" that could happen. This is going in a winter rental, no idea who or what will be operating the stove.
     
    wildwest likes this.
  4. papadave

    papadave

    Joined:
    Oct 3, 2013
    Messages:
    18,181
    Likes Received:
    82,470
    Location:
    Right where I want to be.
    Some say use s/w so you're getting heat off the pipe as well as the stove.
    Some thinking says keep the heat in the pipe to improve draft.
    Good luck to him with part time renters running a stove. How's his firewood? If it were me, I'd be checking the pipe to make sure it wasn't getting clogged up, as you can still do that even with better firewood when using less than ideal burning methods.
    Just my thoughts.
     
    Beetle-Kill and wildwest like this.
  5. MightyWhitey

    MightyWhitey

    Joined:
    Sep 28, 2014
    Messages:
    1,746
    Likes Received:
    6,311
    Location:
    5 miles South of the "cheddar curtain".
    JMNTBHO; but I would never rent a house to renters that had a wood stove in it. Way, way, way too much to go wrong!!!
     
  6. Beetle-Kill

    Beetle-Kill

    Joined:
    Nov 23, 2013
    Messages:
    4,102
    Likes Received:
    19,559
    Location:
    Near the Divide, Colorado
    Luckily he has a local company that is on contract to clean the flue pipe. Good thing too, it's about a 9/12 or 10/12 pitch roof. I didn't offer to help with that.
     
  7. Beetle-Kill

    Beetle-Kill

    Joined:
    Nov 23, 2013
    Messages:
    4,102
    Likes Received:
    19,559
    Location:
    Near the Divide, Colorado
    I hear you! I shudder to think about it, but- oh well. :rolleyes:
     
  8. bobdog2o02

    bobdog2o02

    Joined:
    Nov 19, 2015
    Messages:
    3,005
    Likes Received:
    10,407
    Location:
    Drury Lane, PA
    One word..... insurance
     
    wildwest and Beetle-Kill like this.
  9. CenterTree

    CenterTree

    Joined:
    Mar 15, 2014
    Messages:
    98
    Likes Received:
    379
    Location:
    West central ,PA
    Wood stove for renters??:pain:

    Personally I would want the 6 inch all the way up.
    But being that there is a good chance that his 30-NC is gonna be a glob of molten metal in a few weeks anyway, he might as well just save the money and leave the 8 inch in place.:p
     
    wildwest, papadave and Beetle-Kill like this.
  10. bocefus78

    bocefus78

    Joined:
    Oct 14, 2013
    Messages:
    3,694
    Likes Received:
    19,839
    Location:
    Indiana
    Imo, I'd go liner all the way down.

    I'd also make sure the place has adequate insurance and require the renters to show you proof of renters insurance for their contents.

    Tenants don't even get a gas stove in my family's rentals.

    You are a braver man than I am bk.
     
    wildwest and Beetle-Kill like this.
  11. Beetle-Kill

    Beetle-Kill

    Joined:
    Nov 23, 2013
    Messages:
    4,102
    Likes Received:
    19,559
    Location:
    Near the Divide, Colorado
    Met with him tonight. Pointed him in the direction of an established stove shop in Breckenridge. Told him to go over the options. Let them add some direction concerning the liner vs. 6"- 8" increaser and hoping for the best. I'm trying to distance myself from being the "authority", 'cause I'm not that guy.
    I'll help install stuff if everyone is on board with the same idea.
     
    CenterTree, wildwest and papadave like this.
  12. wildwest

    wildwest Moderator

    Joined:
    Jul 21, 2014
    Messages:
    30,146
    Likes Received:
    141,406
    Location:
    Wyoming high plains
    Does the owner have a heat source beyond the wood stove? If so depending on the length of rental I might guess they will use a furnace for heat and the stove for ambiance.
     
    Beetle-Kill likes this.
  13. HDRock

    HDRock

    Joined:
    Oct 4, 2013
    Messages:
    17,249
    Likes Received:
    60,361
    Location:
    Grand Blanc, MI,
    I run an 8-inch chimney with 6-inch pipe to the ceiling, straight up , about 16 feet total from top of stove, works for me, clean the chimney once a year
     
    wildwest and Beetle-Kill like this.
  14. Beetle-Kill

    Beetle-Kill

    Joined:
    Nov 23, 2013
    Messages:
    4,102
    Likes Received:
    19,559
    Location:
    Near the Divide, Colorado
    update-
    The 30 is on a pedestal, so we lifted it with some 3" square tube to allow air flow, because the hearth darn sure didn't have the required R-value protection. Might even have to add more clearance, not sure. Thoughts?
    He went single wall to the 8". Going through break in fires right now and no evident leakage. Even though it's warm (upper 50s), it's drawing ok.

    I recommended 2 thermometers, one stove top, the other a flue probe. I've only used the probe in double wall stove pipe, any issues with single wall?
    I'll know more next week when he does a full load , Thanks, JB
     
    wildwest likes this.
  15. bobdog2o02

    bobdog2o02

    Joined:
    Nov 19, 2015
    Messages:
    3,005
    Likes Received:
    10,407
    Location:
    Drury Lane, PA
    Single wall pipe should get a surface only thermometer. They are calibrated differently than the probes. One magnetic on the pipe, another on the stove:salute:
     